Sprung Training Message Boards  
Subject: cast iron sectional
Prev Next
You are not authorized to post a reply.

Author Messages
sunrayfarmUser is Offline
Novice Member
Novice Member
Posts:2

02/12/2010 9:41 AM  

I found this American Standard cast iron boiler at a local church and they were kind enough to let me play with it. I found soot under two of the five cast sections in just a small area. Does this indicate a leak? The rest of the boiler looks clean. Little flakes of carbon seem to be leaking out intermittently at the breeching when the ID fan is operating. Could this be a result of the sooting or is it indicitive of  another problem? The boiler is located in the basement in an interior room. The air supply is a 10" duct. Is this adequate?












ReedUser is Offline
Very Active Member
Very Active Member
Posts:179

10/25/2010 7:27 AM  
I apologize for the long delay on this. I'm supposed to get emails notifying me when someone posts, but it didn't work this time.

Does there appear to be adequate supply air to the boiler room? These problems look like a lack of oxygen. There is no leak. If there was, water would be leaking out. An accumulation of soot just indicates incomplete combustion, which means not enough air. There is no way for me to determine whether or not a 10" duct is big enough. My assumption would be that it is. A more common problem is lack of air supply to the boiler room. There should be a big vent hole in the wall with louvers in it or even one with a supply fan. If there is a fan, is it working?

Reed
You are not authorized to post a reply.
Forums > Boiler Plant Training > Pictures! > cast iron sectional



ActiveForums 3.7

You must be registered and logged in to post a comment.  More message boards are available at: SprungServices.com.

 

NOTICE:

Information provided in these message boards is not necessarily the opinion of Sprung Services, Inc.  These discussion boards are provided as a free service to the boiler operations community to promote the free exchange of ideas and to provide assistance from one boiler operator to another as they see fit. 

Sprung Services accepts no responsibility nor guarantees the accuracy of any posts in these message boards. 



  • Need help with boiler operations? 
  • Do you need a job? 

We can help.

 

Sprung Services

 

Phone: (651) 697-0334
Fax: (651) 697-0435

Sprung Services, Inc.
151 Silver Lake Road
Suite 120
New Brighton, MN 55112

register@sprungtraining.com